Old June 25th, 2007, 09:41 PM   #1
Fatty Matty
Senior Member
 
Fatty Matty's Avatar
 
Join Date: 01-05-06
Location: Tecumseh
Posts: 5,357
iTrader: (10)
Mentioned: 0 Post(s)
Default Need help from someone with a NEC book.

I've looked all over online, and can't find an answer to this one. My questions apply to an inground swimming pool.

1. Wet Niche Luminary. Code says a 8gauge ground must be fixed to the inside of the luminary with a potting compound and run through the conduit back to the junction box. The light already has a ground of it's own that runs to the junction box, then the panel.

Well, the niche I'm working is plastic, and has a ground post on the outside of the niche, allowing you to run the ground to a grounding rod, but code that I've seen so far makes no mention of being able to utilize the post on the outside of the niche.

IF you are able to do this, What is the minimum/maximum distance the ground rod must be from the pool.

2. All diving boards, ladders etc must be grounded. Alright. Again, makes no reference as to how far the the rod must be from the pool, and if the ladder
and board can go to the same ground rod.

I've been looking through what I can all day online, but those are the two stumpers. Inspection is either tomorrow night or wednesday night, and I don't like being told something isn't right. I've already had to redo a good chunk of what the electrician did last year.

Any help is greatly appreciated.
__________________
'12 JKU
'14 1500
www.midwest-abs.com
Fatty Matty is online now   Reply With Quote
Sponsored Links
Advertisement
 
Old June 25th, 2007, 09:46 PM   #2
clarkstoncracker
lol
 
clarkstoncracker's Avatar
 
Join Date: 11-03-05
Location: OC - MI
Posts: 42,442
iTrader: (40)
Mentioned: 96 Post(s)
Send a message via AIM to clarkstoncracker
Default



The "bathing" area codes are stupid. They confuse me, that is the only part of the NEC I don't understand.
__________________
clarkstoncracker is offline   Reply With Quote
Old June 25th, 2007, 09:59 PM   #3
Fatty Matty
Senior Member
 
Fatty Matty's Avatar
 
Join Date: 01-05-06
Location: Tecumseh
Posts: 5,357
iTrader: (10)
Mentioned: 0 Post(s)
Default

Quote:
Originally Posted by clarkstoncracker View Post


The "bathing" area codes are stupid. They confuse me, that is the only part of the NEC I don't understand.
It sucks because most electrical code is fairly simple and straigtforward, but this pool shit is really racking my brain. I understand the need for everything they call for, such as EVERYTHING being grounded and GFI'd, but WTF, I don't want to pound a rod into the ground to be told at inspection that it's too far/close, fail, then wait a week for him to come back.

Especially when code doesn't really tell you where it needs to be.
__________________
'12 JKU
'14 1500
www.midwest-abs.com
Fatty Matty is online now   Reply With Quote
Old June 25th, 2007, 10:05 PM   #4
Sandals
Fucking Zen as Shit
 
Sandals's Avatar
 
Join Date: 11-05-05
Location: Lindenhurst, IL
Posts: 15,316
iTrader: (7)
Mentioned: 1 Post(s)
Default

MY pool light is wired with 8 gauge water exposed something or other romex. Switch is located back by the pool filter/pump etc a good 20 feet from the pool. Light is grounded to switch box with a bare copper ground coming out and running to a grounding rod.

Diving board, and ladders simply go into metal sockets in the concrete, i got the pool with the house, but there is no other grounding that i can tell.


Go to your local pool supply/installer and ask them, i'm sure they will know. The one by me is very knowledgeable and always helpful
Sandals is offline   Reply With Quote
Old June 25th, 2007, 10:16 PM   #5
Fatty Matty
Senior Member
 
Fatty Matty's Avatar
 
Join Date: 01-05-06
Location: Tecumseh
Posts: 5,357
iTrader: (10)
Mentioned: 0 Post(s)
Default

Well, a local pool company is finishing the pool, but refuse to touch the electric, and the faggots can never be found or heard from when you need any sort of technical help. Fuck it, I can't even begin to explain how screwed this whole pool thing has been. The company, who I won't mention yet, is the most jacked operation I've ever seen. Dickheads filled the pool without putting the light in. They were supposed to be out today to install the light in the niche, but never showed. We called and asked WTF was going on, and was told that somebody was sick. Whatever. I almost pulled out the rape card.
__________________
'12 JKU
'14 1500
www.midwest-abs.com
Fatty Matty is online now   Reply With Quote
Reply
Great Lakes 4x4. The largest offroad forum in the Midwest > General 4x4 Stuff > The Pub

Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 11:04 AM.


Powered by: vBulletin, Copyright 2000 - 2012, Jelsoft Enterprises Ltd.
User Alert System provided by Advanced User Tagging (Lite) - vBulletin Mods & Addons Copyright © 2014 DragonByte Technologies Ltd. Runs best on HiVelocity Hosting.
Page generated in 0.13680 seconds with 35 queries