Quote:
Originally Posted by ljense8 View Post
A check valve by the pump will keep the water from back flushing.
Right. So, if that one is bad, right now, as we speak, his pressure tank is power back flushing his point. That equals sink hole birthing, which is bad. Installing a check valve any where (like in the house, right in front of the pressure tank, which is what it sounds like you were implying) would stop the pressure tank from bleeding down, but the line between the check valve and the pump would still trickle back, and the pump would have to refill the line every time it had to cycle on.

I think you need to pull your pump Aaron. Until you are able to, I would shut the valve between your pressure tank and the pump, when you don't need water.
MonkeyBiz is offline   Reply With Quote
Old September 15th, 2013, 05:59 PM   #22
ljense8
Web Wheeler
 
ljense8's Avatar
 
Join Date: 01-16-13
Location: Holland, MI
Posts: 533
iTrader: (2)
Mentioned: 0 Post(s)
Default

The pipe will not trickle back unless there is an air break somewhere in the line. In order for the pipe to empty and fill with air, there has to be a way for air to enter it. If the pipe is perforated, then this could happen, but in this case, replacing the current check will not help, he would have to replace the whole pipe. He could replace just the leaky section, but that would require unions in the pipe, which tend to leak. If it's just a leaky check valve, the water will not have a way to trickle out.

Last edited by ljense8; September 15th, 2013 at 06:03 PM.
ljense8 is offline   Reply With Quote
Old September 15th, 2013, 06:14 PM   #23
ljense8
Web Wheeler
 
ljense8's Avatar
 
Join Date: 01-16-13
Location: Holland, MI
Posts: 533
iTrader: (2)
Mentioned: 0 Post(s)
Default

I do agree about stopping the flow going back ASAP, if that is where it is actually going. Sink holes are no bueno, especially by your house.
ljense8 is offline   Reply With Quote
Old September 15th, 2013, 07:26 PM   #24
amc78cj7
Senior Member
 
amc78cj7's Avatar
 
Join Date: 11-07-05
Location: Ann Arbor, MI
Posts: 5,352
iTrader: (9)
Mentioned: 0 Post(s)
Default

When we bought our house it was short cycling due to low pressure. Hooked up a compressor and added air to the tank. Haven't had a problem since. That was 3 years ago.
__________________
I'm not quoting idiots who promote unsafe recovery strap techniques anymore. :miff:
amc78cj7 is offline   Reply With Quote
Old September 15th, 2013, 07:35 PM   #25
HVYRTFT
Reed my teef
 
HVYRTFT's Avatar
 
Join Date: 01-17-07
Location: Whitehall,MI
Posts: 2,404
iTrader: (9)
Mentioned: 1 Post(s)
Default

There was not a check valve where the line comes in through the wall and then goes to the pressure tank. Every picture I have seen shows one there. I just got done installing one and now it works like it should.
So...
Did I just fix something that was never done properly in the first place or was that fix just a band aid for a bigger problem?

I'm saying there is no other major problem because nothing acted like there was any broken pipes. No leaks, good pressure, water on demand, no evidence of water where it shouldn't be, etc.
HVYRTFT is offline   Reply With Quote
Old September 15th, 2013, 07:48 PM   #26
ljense8
Web Wheeler
 
ljense8's Avatar
 
Join Date: 01-16-13
Location: Holland, MI
Posts: 533
iTrader: (2)
Mentioned: 0 Post(s)
Default

It's hard to answer your question online. It was probably a leaky check valve by the pump. If so, you should be good. If you were leaking pressure through a perforated or cracked pipe, your pipe will trickle back, like Monkey Biz said. One way to check is to time how long it takes to get up to pressure. If it takes a long time to pressure up, the pipe is probably leaking. This is not a certain check though. It would be best to inspect your pipe to be sure. Chances are, you are good to go, but it wouldn't hurt to be certain.
ljense8 is offline   Reply With Quote
Old September 15th, 2013, 07:50 PM   #27
High Center Hancho
rack tap re-rack click
 
High Center Hancho's Avatar
 
Join Date: 07-10-07
Location: Genesee County
Posts: 12,713
iTrader: (40)
Mentioned: 0 Post(s)
Default

Now you guys have me thinking I should install a check valve
High Center Hancho is offline   Reply With Quote
Old September 15th, 2013, 07:54 PM   #28
ljense8
Web Wheeler
 
ljense8's Avatar
 
Join Date: 01-16-13
Location: Holland, MI
Posts: 533
iTrader: (2)
Mentioned: 0 Post(s)
Default

Hancho, if you have a pressure tank, you have a check valve. The only real advantage to having a check valve by the tank is ease if maintenance. It's slightly easier to access things when they are right in your house.
ljense8 is offline   Reply With Quote
Old September 15th, 2013, 07:57 PM   #29
High Center Hancho
rack tap re-rack click
 
High Center Hancho's Avatar
 
Join Date: 07-10-07
Location: Genesee County
Posts: 12,713
iTrader: (40)
Mentioned: 0 Post(s)
Default

Quote:
Originally Posted by ljense8 View Post
Hancho, if you have a pressure tank, you have a check valve. The only real advantage to having a check valve by the tank is ease if maintenance. It's slightly easier to access things when they are right in your house.
I do at the pump, and every now and then, it leaks backs...I've only noticed it twice, normally it holds pressure
High Center Hancho is offline   Reply With Quote
Old September 15th, 2013, 08:07 PM   #30
ljense8
Web Wheeler
 
ljense8's Avatar
 
Join Date: 01-16-13
Location: Holland, MI
Posts: 533
iTrader: (2)
Mentioned: 0 Post(s)
Default

Sounds like it's probably fine.
ljense8 is offline   Reply With Quote
Old September 15th, 2013, 10:22 PM   #31
ckupq
Kitten I'm gonna eat you!
 
ckupq's Avatar
 
Join Date: 11-07-05
Location: Cedar Rapids, IA 52402
Posts: 3,381
iTrader: (6)
Mentioned: 0 Post(s)
Default

I'm LOLing at the comments there are more things to check than just a flapper valve.

For Starters:
The buried pipe to the well.
The transition from the buried pipe to the well.
The transition to the pipe inside the well.
The pipe inside the well.
The flapper valve.


My father's well wasn't buried right and was causing water to leak on the outside of the well. It caused us to dig for 2 hours till we could get a hole big enough to fix it. His rental had issues the year before with the O-ring on the brass transition piece inside the well. The well sounded like it had a running fire hose in it.

IMHO Working on a well isn't that hard, just tough and a multi-person job. Pulling a well takes 5 minutes and two people if done right. My father's 77 and we can still pull his 75ft deep well by hand. Its just like any other plumbing job except its in a casing. Good luck.
ckupq is offline   Reply With Quote
Old September 16th, 2013, 08:33 AM   #32
Haggar
Covered in mud...
 
Haggar's Avatar
 
Join Date: 11-06-05
Location: Oxford, MI
Posts: 17,546
iTrader: (54)
Mentioned: 1 Post(s)
Default

Typical system is:

Well pump
check valve
drop tube
seal to well casing
pipe from well casing to house
pressure switch
well tank
shut off valve to house plumbing

If you shut off the supply valve from the well tank to the house, and the well still cycles repeatedly, then you have a leak outside the house. Either the check valve is leaking, or the pipes.
Haggar is offline   Reply With Quote
Old September 16th, 2013, 08:34 AM   #33
Haggar
Covered in mud...
 
Haggar's Avatar
 
Join Date: 11-06-05
Location: Oxford, MI
Posts: 17,546
iTrader: (54)
Mentioned: 1 Post(s)
Default

Don't add a check valve at the tank as a bandaid. A check valve at the pump is all thats needed, if that isn't working, there's a leak, and adding a second valve just covers it up.
Haggar is offline   Reply With Quote
Old September 16th, 2013, 03:55 PM   #34
redmosquito1
Senior Member
 
redmosquito1's Avatar
 
Join Date: 09-23-07
Location: Clarkston, MI
Posts: 578
iTrader: (1)
Mentioned: 0 Post(s)
Default

I don't know if this was mentioned or not but my moms well was doing what you described a few weeks back before it finally killed a brand new pump my dad had replaced a few years ago right before he died. What happened was the membrane in the pressure tank failed, I don't know squat about wells so you may have already checked but it's possible your failed too.

New pump and new tank and now she has no problems.

Just a thought.
redmosquito1 is offline   Reply With Quote
Old September 16th, 2013, 04:07 PM   #35
Buggy_Tim
(513) 891-8372
 
Buggy_Tim's Avatar
 
Join Date: 11-05-05
Location: Sault Sainte Marie
Posts: 11,699
iTrader: (12)
Mentioned: 2 Post(s)
Default

How does one know if their pump is cycling more than it should?
Buggy_Tim is offline   Reply With Quote
Old September 16th, 2013, 04:13 PM   #36
MonkeyBiz
Master Cocksman
 
MonkeyBiz's Avatar
 
Join Date: 11-06-05
Location: Whitehall
Posts: 8,242
iTrader: (10)
Mentioned: 3 Post(s)
Send a message via Yahoo to MonkeyBiz
Default

if the well is running, when you haven't been flowing any water. His was running every 11 min.
MonkeyBiz is offline   Reply With Quote
Old September 16th, 2013, 04:23 PM   #37
Buggy_Tim
(513) 891-8372
 
Buggy_Tim's Avatar
 
Join Date: 11-05-05
Location: Sault Sainte Marie
Posts: 11,699
iTrader: (12)
Mentioned: 2 Post(s)
Default

I would have to go outside and put my ear on the well head to hear it run I think. It's like way down in a hole. I never hear mine run. That's why I was asking.
Buggy_Tim is offline   Reply With Quote
Old September 16th, 2013, 04:28 PM   #38
MonkeyBiz
Master Cocksman
 
MonkeyBiz's Avatar
 
Join Date: 11-06-05
Location: Whitehall
Posts: 8,242
iTrader: (10)
Mentioned: 3 Post(s)
Send a message via Yahoo to MonkeyBiz
Default

His, like mine has the pump down the well. I can't hear it when I'm outside, but I still easily hear mine kick on and off if there is water flowing when I'm inside. He didn't realize it wasn't supposed to do that. It wasn't until a friend of his came over, that he realized it. Silly city boy.
MonkeyBiz is offline   Reply With Quote
Old September 16th, 2013, 06:46 PM   #39
jeepfreak81
81 inches of fun
 
jeepfreak81's Avatar
 
Join Date: 11-10-05
Location: Lennon, Mi
Posts: 12,148
iTrader: (21)
Mentioned: 0 Post(s)
Send a message via AIM to jeepfreak81 Send a message via MSN to jeepfreak81 Send a message via Yahoo to jeepfreak81
Default

Quote:
Originally Posted by MonkeyBiz View Post
His, like mine has the pump down the well. I can't hear it when I'm outside, but I still easily hear mine kick on and off if there is water flowing when I'm inside. He didn't realize it wasn't supposed to do that. It wasn't until a friend of his came over, that he realized it. Silly city boy.
I thought he was Amish....




jeepfreak81 is offline   Reply With Quote
Old September 16th, 2013, 07:51 PM   #40
MonkeyBiz
Master Cocksman
 
MonkeyBiz's Avatar
 
Join Date: 11-06-05
Location: Whitehall
Posts: 8,242
iTrader: (10)
Mentioned: 3 Post(s)
Send a message via Yahoo to MonkeyBiz
Default

Quote:
Originally Posted by jeepfreak81 View Post
I thought he was Amish....




He converted. He has a little black boy that rides a bike in the shed to power the well.
MonkeyBiz is offline   Reply With Quote
Reply
Great Lakes 4x4. The largest offroad forum in the Midwest > General 4x4 Stuff > The Pub
Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump



All times are GMT -5. The time now is 01:34 PM.


Powered by: vBulletin, Copyright 2000 - 2012, Jelsoft Enterprises Ltd.
User Alert System provided by Advanced User Tagging (Lite) - vBulletin Mods & Addons Copyright © 2014 DragonByte Technologies Ltd. Runs best on HiVelocity Hosting.
Copyright 2005 - 2012 Cracker Enterprises - Powered by Linux
vB Ad Management by =RedTyger=
Page generated in 0.20536 seconds with 50 queries