Need 480 3 phase help *problem solved* - Great Lakes 4x4. The largest offroad forum in the Midwest
Old September 18th, 2012, 05:55 PM   #1
chadcooper55
expert jeep disassembler
chadcooper55's Avatar
Default Need 480 3 phase help *problem solved*
In my barn I have a 60a 480 3 phase service but it is an old style 3 phase. If you go from hot to ground one is 615v the next is 350v and the other is 250v. If you go from hot to hot it reads 490v between any of them. The only 110v I have is through a small transformer. Is there any way that I can run a 480 single phase piece of equiptment off this power. In my opinion the power looks great as 3 phase it just makes me nervous to hook anything else up other than that. Also how do I tell how much power the transformer is kicking out? It doesn't say in normal persons terms anywhere on it. It can't be much because there is only 2 12g wires coming from the 2 hottest legs of the three phase to the transformer. I am used to standard delta 3 phase that is 277v from each hot to the ground. The closest I can guess I have some type of wild leg old school 3 phase. I am not smart with electrical but I am used to wiring in temporary welder and pump pigtails into disconnects and things like that.
Old September 18th, 2012, 06:06 PM   #2
sparkman10mm
sparkman10mm's Avatar
What is your voltage phase to phase? 480-490..gtg..
With 3 phase 3 wire system, your voltage phase to ground is not applicable. There is no neutral conductor.
What type 480 single phase equipment are you wanting to run?
BTW the 277/480 system is a 4 wire wye (not delta)system with a grounded neutral.
sparkman10mm is offline   Reply With Quote
Old September 18th, 2012, 06:11 PM   #3
chadcooper55
Type t-2794-h
Pri volts 240x480
Sec volts 120/240
Cycles 60
Kva 5 continuous
At 150*c rise
Approx imped at 75* c 4.5%
Approx weight 114 lbs
Serial no. 37681
Leads from 3ph go to h4 and h1
X1 and x4 go to the 110/240
X2 and x3 go to ground
H2 and h3 are jumpered together
Old September 18th, 2012, 06:12 PM   #4
chadcooper55
Also it is an acme single phase transformer.
Old September 18th, 2012, 06:25 PM   #5
chadcooper55
All I know is the stuff I wire in every day has 3 hots that are 277 to ground and are around 440-490 from hot to hot depending on the plant I am working in. That is the standard 3 phase in industrial plants around the country. I know of a few other old places with the exact same power as I have that run 3 phase equiptment off it. Mainly I would like to run a single phase 440v or 220v welder. My mill, saw, drill, grinder, ect are all 3 phase.
Old September 18th, 2012, 06:40 PM   #6
chadcooper55
As I understand 3 phase delta is 3 hots and no neutral with a ground and is 277 from hot to ground. Y is 3 hots, 1 neutral and a ground. I could be wrong but that is what is coming to mind.
Old September 18th, 2012, 09:14 PM   #7
firehawk
Live Action!
firehawk's Avatar
http://en.wikipedia.org/wiki/Three-phase_electric_power
Three-phase electric power is a common method of alternating-current electric power generation, transmission, and distribution.[1] It is a type of polyphase system and is the most common method used by electrical grids worldwide to transfer power. It is also used to power large motors and other heavy loads. A three-phase system is generally more economical than others because it uses less conductor material to transmit electric power than equivalent single-phase or two-phase systems at the same voltage.[2] The three-phase system was invented by Galileo Ferraris and Nikola Tesla in 1887 and 1888.
In a three-phase system, three circuit conductors carry three alternating currents (of the same frequency) which reach their instantaneous peak values at different times. Taking one conductor as the reference, the other two currents are delayed in time by one-third and two-thirds of one cycle of the electric current. This delay between phases has the effect of giving constant power transfer over each cycle of the current and also makes it possible to produce a rotating magnetic field in an electric motor.
Three-phase systems may have a neutral wire. A neutral wire allows the three-phase system to use a higher voltage while still supporting lower-voltage single-phase appliances. In high-voltage distribution situations, it is common not to have a neutral wire as the loads can simply be connected between phases (phase-phase connection).
Three-phase has properties that make it very desirable in electric power systems:
The phase currents tend to cancel out one another, summing to zero in the case of a linear balanced load. This makes it possible to eliminate or reduce the size of the neutral conductor; all the phase conductors carry the same current and so can be the same size, for a balanced load.
Power transfer into a linear balanced load is constant, which helps to reduce generator and motor vibrations.
Three-phase systems can produce a magnetic field that rotates in a specified direction, which simplifies the design of electric motors.
Three is the lowest phase order to exhibit all of these properties.
Most household loads are single-phase. In North America and a few other places, three-phase power generally does not enter homes. Even in areas where it does, it is typically split out at the main distribution board and the individual loads are fed from a single phase. Sometimes it is used to power electric stoves and electric clothes dryers.
The three phases are typically indicated by colours which vary by country. See the table for more information.
Contents [hide]
1 Generation and distribution
2 Three-wire versus four-wire
3 Out-of-balance loads
4 Single-phase loads
5 Three-phase loads
6 Phase converters
7 Alternatives to three-phase
8 Colour codes
9 See also
10 References
[edit]Generation and distribution
Animation of three-phase current flow
Left: Elementary six-wire three-phase alternator, with each phase using a separate pair of transmission wires.[3] Right: Elementary three-wire three-phase alternator, showing how the phases can share only three wires.[4]
At the power station, an electrical generator converts mechanical power into a set of three AC electric currents, one from each coil (or winding) of the generator. The windings are arranged such that the currents vary sinusoidally at the same frequency but with the peaks and troughs of their wave forms offset to provide three complementary currents with a phase separation of one-third cycle (120° or 2π⁄3 radians). The generator frequency is typically 50 or 60 Hz, varying by country.
Further information: Mains power systems
Large power generators provide an electric current at a potential which can be a few hundred volts or up to about 30 kV. At the power station, transformers step this voltage up to one suitable for transmission.
After numerous further conversions in the transmission and distribution network, the power is finally transformed to the standard utilization voltage for lighting and equipment. Single-phase loads are connected from one phase to neutral or between two phases. Three-phase loads such as larger motors must be connected to all three phases of the supply.
[edit]Three-wire versus four-wire
Three-phase circuits occur in two varieties: three-wire and four-wire. Both types have three energized ("hot" or "live") wires, but the 4-wire circuit also has a neutral wire. The three-wire system is used when the loads on the 3 live wires will be balanced, for example in motors or heating elements with 3 identical coils.
The neutral wire is essential when there is a chance that the loads are not balanced. A common example is seen in local distribution in Europe, where each house is connected to just one of the live wires, but each house's neutral wire is connected to one common neutral. When neighbouring houses draw unequal powers, the common neutral wire carries a current as a result of the imbalance. Hence electrical engineers work to make sure that the power is divided equally, so the neutral wire carries as little current as possible and therefore wastes little power. Obviously it is statistically easier to produce a good balance when supplying power to a large number of houses, so any large imbalances tend to be confined to small localities around a few houses.
The '3-wire' and '4-wire' designations do not count the ground wire used on many transmission lines which is solely for fault and lightning protection and does not serve to deliver power.
[edit]Out-of-balance loads
When the currents on the three live wires of a three-phase system are not of equal amplitude or do not have the correct phases, the power-loss is greater than for a perfectly balanced system. The degree of imbalance is expressed by symmetrical components. Three-phase systems are evaluated at generating stations and substations in terms of these three components, of which two are zero in a perfectly balanced system.
[edit]Single-phase loads
Single-phase loads may be connected to a three-phase system in two ways. Either a load may be connected across two of the live conductors, or a load can be connected from a live phase conductor to the neutral conductor. Single-phase loads should be distributed evenly between the phases of the three-phase system for efficient use of the supply transformer and supply conductors. If the line-to-neutral voltage is a standard load voltage, for example 230 volt on a 400 volt three-phase system, single-phase loads can connect to a phase and the neutral. Loads can be distributed over three phases to balance the load. Where the line-to-neutral voltage is not the standard voltage for example 347 volts produced by a 600 V system, single-phase loads are connected through a step-down transformer.
In a symmetrical three-phase system, the system neutral has the same magnitude of voltage to each of the three-phase conductors. The voltage between line conductors (Vl) is √3 times the phase conductor to neutral voltage (Vp). That is: Vl = √3Vp.
In some multiple-unit residential buildings of North America, three-phase power is supplied to the building but individual units have only single-phase power formed from two of the three supply phases. Lighting and convenience receptacles are connected from either phase conductor to neutral, giving the usual 120 V required by typical North American appliances. In the split-phase system, high-power loads are connected between the opposite "hot" poles, giving a voltage of 240 V. In some cases, they may be connected between phases of a three-phase system, giving a voltage of 208 V. This practice is common enough that 208 V single-phase equipment is readily available in North America. Attempts to use the more common 120/240 V equipment intended for split-phase distribution may result in poor performance since 240 V heating and lighting equipment will only produce 75% of its rating when operated at 208 V. Motors rated at 240 V will draw higher current at 208 V; some motors are dual-labelled for both voltages.
Where three-phase at low voltage is otherwise in use, it may still be split out into single-phase service cables through joints in the supply network or it may be delivered to a master distribution board (breaker panel) at the customer's premises. Connecting an electrical circuit from one phase to the neutral generally supplies the standard single phase voltage to the circuit (either 120 V AC or 230 V AC depending on the regional standard).
The currents returning from the customers' premises to the supply transformer all share the neutral wire. If the loads are evenly distributed on all three phases, the sum of the returning currents in the neutral wire is approximately zero. Any unbalanced phase loading on the secondary side of the transformer will use the transformer capacity inefficiently.
If the supply neutral of a three-phase system with line-to-neutral connected loads is broken, the voltage balance on the loads will no longer be maintained. The neutral point will tend to drift toward the most heavily loaded phase, causing undervoltage conditions on that phase and overvoltage on a lightly loaded phase; the lightly loaded phases may approach the line-to-line voltage, which exceeds the line-to-neutral voltage by a factor of √3, causing overheating and failure of many types of loads.
For example, if several houses are connected through a 240 V transformer, which is connected to one phase of the three-phase system, each house might be affected by the imbalance on the three-phase system. If the neutral connection is broken somewhere in the system, all equipment in a house might be damaged due to over-voltage. A similar phenomenon can exist if the house neutral (connected to the center tap of the 240 V pole transformer) is disconnected. This type of failure event can be difficult to troubleshoot if the drifting neutral effect is not understood. With inductive and/or capacitive loads, all phases can suffer damage as the reactive current moves across abnormal paths in the unbalanced system, especially if resonance conditions occur. For this reason, neutral connections are a critical part of a power distribution network and must be made as reliable as any of the phase connections.
Where a mixture of single-phase 120-volt lighting and three-phase, 240-volt motors are to be supplied, a system called high-leg delta is used.
[edit]Three-phase loads
A transformer for a high-leg delta system; 240 V 3-phase motors would be connected to L1, L2 and L3. Single-phase lighting would be connected L1 or L2 to neutral (N). No loads would be connected from L3 (the high or wild leg) to neutral, since the voltage would be 208 V.
The most important class of three-phase load is the electric motor. A three-phase induction motor has a simple design, inherently high starting torque and high efficiency. Such motors are applied in industry for pumps, fans, blowers, compressors, conveyor drives, electric vehicles and many other kinds of motor-driven equipment. A three-phase motor is more compact and less costly than a single-phase motor of the same voltage class and rating and single-phase AC motors above 10 HP (7.5 kW) are uncommon. Three-phase motors also vibrate less and hence last longer than single-phase motors of the same power used under the same conditions.
Resistance heating loads such as electric boilers or space heating may be connected to three-phase systems. Electric lighting may also be similarly connected. These types of loads do not require the revolving magnetic field characteristic of three-phase motors but take advantage of the higher voltage and power level usually associated with three-phase distribution. Legacy single-phase fluorescent lighting systems also benefit from reduced flicker in a room if adjacent fixtures are powered from different phases.
Large rectifier systems may have three-phase inputs; the resulting DC is easier to filter (smooth) than the output of a single-phase rectifier. Such rectifiers may be used for battery charging, electrolysis processes such as aluminium production or for operation of DC motors.
One example of a three-phase load is the electric arc furnace used in steelmaking and in refining of ores.
In much of Europe, stoves are designed for a three-phase feed. Usually the individual heating units are connected between phase and neutral to allow for connection to a single-phase supply. In many areas of Europe, single-phase power is the only source available.
[edit]Phase converters
Occasionally the advantages of three-phase motors make it worthwhile to convert single-phase power to three-phase. Small customers, such as residential or farm properties, may not have access to a three-phase supply or may not want to pay for the extra cost of a three-phase service but may still wish to use three-phase equipment. Such converters may also allow the frequency to be varied (resynthesis) allowing speed control. Some railway locomotives are moving to multi-phase motors driven by such systems even though the incoming supply to a locomotive is nearly always either DC or single-phase AC.
Because single-phase power goes to zero at each moment that the voltage crosses zero but three-phase delivers power continuously, any such converter must have a way to store the necessary energy for a fraction of a second.
One method for using three-phase equipment on a single-phase supply is with a rotary phase converter, essentially a three-phase motor with special starting arrangements and power factor correction that produces balanced three-phase voltages. When properly designed, these rotary converters can allow satisfactory operation of three-phase equipment such as machine tools on a single-phase supply. In such a device, the energy storage is performed by the mechanical inertia (flywheel effect) of the rotating components. An external flywheel is sometimes found on one or both ends of the shaft.
A second method that was popular in the 1940s and 1950s was the transformer method. At that time, capacitors were more expensive than transformers, so an autotransformer was used to apply more power through fewer capacitors. This method performs well and does have supporters, even today. The usage of the name transformer method separated it from another common method, the static converter, as both methods have no moving parts, which separates them from the rotary converters.
Another method often attempted is with a device referred to as a static phase converter. This method of running three-phase equipment is commonly attempted with motor loads though it only supplies ⅔ power and can cause the motor loads to run hot and in some cases overheat. This method does not work when sensitive circuitry is involved such as CNC devices or in induction and rectifier-type loads.
A three-phase generator can be driven by a single-phase motor. This motor-generator combination can provide a frequency changer function as well as phase conversion, but requires two machines with all their expense and losses. The motor-generator method can also form an uninterruptable power supply when used in conjunction with a large flywheel and a standby generator set.
Some devices are made which create an imitation three-phase from three-wire single-phase supplies. This is done by creating a third "subphase" between the two live conductors, resulting in a phase separation of 180° − 90° = 90°. Many three-phase devices can run on this configuration but at lower efficiency.
Variable-frequency drives (also known as solid-state inverters) are used to provide precise speed and torque control of three-phase motors. Some models can be powered by a single-phase supply. VFDs work by converting the supply voltage to DC and then converting the DC to a suitable three-phase source for the motor.
Digital phase converters are designed for fixed-frequency operation from a single-phase source. Similar to a variable-frequency drive, they use a microprocessor to control solid-state power switching components to maintain balanced three-phase voltages.
[edit]Alternatives to three-phase
Split-phase electric power is used when three-phase power is not available and allows double the normal utilization voltage to be supplied for high-power loads.
Two-phase electric power, like three-phase, gives constant power transfer to a linear load. For loads that connect each phase to neutral, assuming the load is the same power draw, the two-wire system has a neutral current which is greater than neutral current in a three-phase system. Also motors are not entirely linear, which means that despite the theory, motors running on three-phase tend to run smoother than those on two-phase. The generators in the Adams Power Plant at Niagara Falls which were installed in 1895 were the largest generators in the world at the time and were two-phase machines. True two-phase power distribution is basically obsolete. Special-purpose systems may use a two-phase system for control. Two-phase power may be obtained from a three-phase system (or vice versa) using an arrangement of transformers called a Scott-T transformer.
Monocyclic power was a name for an asymmetrical modified two-phase power system used by General Electric around 1897, championed by Charles Proteus Steinmetz and Elihu Thomson. This system was devised to avoid patent infringement. In this system, a generator was wound with a full-voltage single-phase winding intended for lighting loads and with a small fraction (usually ¼ of the line voltage) winding which produced a voltage in quadrature with the main windings. The intention was to use this "power wire" additional winding to provide starting torque for induction motors, with the main winding providing power for lighting loads. After the expiration of the Westinghouse patents on symmetrical two-phase and three-phase power distribution systems, the monocyclic system fell out of use; it was difficult to analyze and did not last long enough for satisfactory energy metering to be developed.
High-phase-order systems for power transmission have been built and tested. Such transmission lines use six (two-pole, three-phase) or twelve (two-pole, six-phase) lines and employ design practices characteristic of extra-high-voltage transmission lines. High-phase-order transmission lines may allow transfer of more power through a given transmission line right-of-way without the expense of a high-voltage direct current (HVDC) converter at each end of the line.
[edit]Colour codes
Conductors of a three-phase system are usually identified by a colour code, to allow for balanced loading and to assure the correct phase rotation for induction motors. Colours used may adhere to International Standard IEC 60446, older standards or to no standard at all and may vary even within a single installation. For example, in the U.S. and Canada, different colour codes are used for grounded (earthed) and ungrounded systems.
L1 L2 L3 Neutral Ground/
protective earth
Australia and New Zealand as per AS/NZS 3000:2007 Figure 3.2 (or as per IEC 60446 as approved by AS:3000) Red (or brown)1 White (or black)1 (prev. yellow) Dark blue (or grey)1 Black (or blue)1 Green/yellow striped (green on very old installations)
Canada (mandatory)[5] Red Black Blue White Green or bare copper
Canada (isolated three-phase installations)[6] Orange Brown Yellow White Green
European Union and all countries who use European CENELEC standards April 2004 (IEC 60446), Hong Kong from July 2007, Singapore from March 2009 Brown Black Grey Blue Green/yellow striped2
Older European (IEC 60446, varies by country3) Black or brown Black or brown Black or brown Blue Green/yellow striped3
UK until April 2006, Hong Kong until April 2009, South Africa, Malaysia, Singapore until February 2011 Red Yellow Blue Black Green/yellow striped (green on installations before c. 1970)
Republic of India and Pakistan Red Yellow Blue Black Green
Former USSR (Russia, Ukraine, Kazakhstan) and People's Republic of China (per GB 50303-2002 Section 15.2.2) Yellow Green Red Light blue Green/yellow striped
Norway Black White/Grey Brown Blue Yellow/green striped, older may be only yellow or bare copper
United States (common practice)4 Black Red Blue White, or grey Green, green/yellow striped,7 or a bare copper wire
United States (alternative practice)5 Brown Orange (delta), violet (wye) Yellow Grey, or white Green
^1 In Australia and New Zealand, active conductors can be any colour except green/yellow, green, yellow, black or light blue. Yellow is no longer permitted in the 2007 revision of wiring code ASNZS 3000. European colour codes are used for all IEC or flex cables such as extension leads, appliance leads etc. and are equally permitted for use in building wiring per AS/NZS 3000:2007.
^2 The international standard green-yellow marking of protective-earth conductors was introduced to reduce the risk of confusion by colour blind installers. About 7% to 10% of men cannot clearly distinguish between red and green, which is a particular concern in older schemes where red marks a live conductor and green marks protective earth or safety ground.
^3 In Europe, there still exist installations with older colours for protective earth but, since the early 1970s, all new installations use green/yellow according to IEC 60446.
^4 See Paul Cook: Harmonised colours and alphanumeric marking. IEE Wiring Matters, Spring 2006.
^5 Since 1975, the U.S. National Electric Code has not specified colouring of phase conductors. It is common practice in many regions to identify 120/208Y conductors as black, red, and blue. Local regulations may amend the N.E.C. The U.S. National Electric Code has colour requirements for grounded conductors, ground and grounded-delta 3-phase systems which result in one ungrounded leg having a higher voltage potential to ground than the other two ungrounded legs. Orange is only appropriate when the system has a grounded delta service, regardless of voltage.
^6 The U.S. National Electric Code does not specify colouring of phase conductors, other than orange for grounded delta. It is common practice in many regions to identify 277/480Y conductors as brown, orange and yellow (delta) or brown, violet and yellow (wye), with orange always being the centre phase. Local practice may amend the N.E.C. The US N.E.C. rule 517.160 (5) states these colors are to be used for isolated power systems in health care facilities. Colour of conductors does not identify voltage of a circuit, because there is no formal standard.
^7 In the U.S., a green/yellow striped wire may indicate an isolated ground.[citation needed] In most countries today, green/yellow striped wire may only be used for protective earth (safety ground) and may never be unconnected or used for any other purpose.
That is all I have off the top of my head.
Old September 18th, 2012, 09:16 PM   #8
firehawk
Live Action!
firehawk's Avatar
This is funny too
I hate being bipolar, its great!
Old September 18th, 2012, 09:56 PM   #9
chadcooper55
blah blah blah
I try to retain a little bit of the knowledge I learn at work. We are always dealing with 3 phase power. I don't understand how it works but I know the little drawings that look like a swirly triangle and Y. I wish I understood what the triangle and Y actually meant.........
Old September 18th, 2012, 10:09 PM   #10
redmosquito1
redmosquito1's Avatar
They mean delta (triangle) and wye (Y). It depicts how the transformer is hooked up, in a delta typically there is no ground and the load is connected phase to phase where in a wye the ground or neutral is in the center and load is connected phase to ground/neutral. Varrying reasons why the difference and where/when it's used I guess but that's what those symbols mean, I am no expert. But in a delta you would see 3 conductors and in wye 4, with a protective ground possible for both.
My math shows your transformer is capable of 40amps at 120v and 20 amps at 240V. That seems low to me so my math is probably off.
redmosquito1 is offline   Reply With Quote
Old September 18th, 2012, 10:26 PM   #11
chadcooper55
I realize that but I don't actually understand it. 40 amps of 120 doesn't sound that far off to me. It isn't very big. I need to talk to consumers about running another service out there. It will need to be there for my new house I am building eventually anyways. I wish transformers wetent so damn expensive or I would get a bigger one.
Old September 19th, 2012, 08:05 AM   #12
sparkman10mm
41.666 amps @120 volt (kva x 1000 divided by voltage)
Your math is close enough.
Old September 19th, 2012, 08:21 AM   #13
redmosquito1
Transformers are confusing unless your an electrical engineer. Lots of info on them online though, lots of talk of vectors and shit so I don't get it very well either.
Old September 19th, 2012, 09:18 AM   #14
chadcooper55
Talked to an electrician on the jobsite I am working at right now and he thinks I will be fine running a single phase machine on it bc I am getting 480ish between the two hots. Thoughts?
Old September 19th, 2012, 02:40 PM   #15
MonkeyBiz
Master Cocksman
MonkeyBiz's Avatar
PM Square D... He ownz this shit.
Old September 19th, 2012, 03:47 PM   #16
parkerinc
parkerinc's Avatar
You can't run your single phase equipment due to the fact you would need a reference to ground. You would need a dry transformer for this.
parkerinc is offline   Reply With Quote
Old September 19th, 2012, 06:03 PM   #17
redmosquito1
Reading your description it sounds like your 3 phase 480v coming into the house is an ungrounded delta, I would think if you hooked up your single phase to 2 of the hots you would be fine. You wouldn't want to go phase to ground because you are not getting 480v.
Old September 19th, 2012, 06:21 PM   #18
chadcooper55
After hearing 10 different stories from 10 people I think I got a solution to all my issues.
First of all the electricians on the jobsite I am working on who deal with 3 phase high voltage power all day don't seem to know what they are talking about I can not run a single phase machine on an unbalanced 3 phase as was said by the last person that commented.
Second I am sick of only having a goofy 3 phase and hardly any 240 or 120.
I found a very nice used, refurbished 50kva transformer for $700 that I think I am going to pick up tomorrow.
I think this will solve all my issues and I will be able to have any type of power that I want to be able to run any equipment I find for a good deal.
Opinions on this?
Old September 19th, 2012, 06:47 PM   #19
ronprice
ronprice's Avatar
To make it easy. Just have a 220 service added. and dont try to adapt the 3 phase. Transformers suck and are costly. Run 3 phase on 3 phase and the rest on its own service.
ronprice is offline   Reply With Quote
Old September 19th, 2012, 07:05 PM   #20
chadcooper55
I can either spend 700 on a transformer right now and use the welders I have or spend 1000 and get a new/used welder. It is also nice than my house and barn power are 2 completely seperate services and if I lose power at my house I still have power in the barn sometimes. I have enough welding extension cords on my truck I can run them to the house and live life like normal, well if I had 220
Page generated in 0.85837 seconds with 82 queries